Adjusting the sensitivity of UPS on a RN312 with ReadyNas 6.5.2
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Adjusting the sensitivity of UPS on a RN312 with ReadyNas 6.5.2
Attached locally to a RN312 is an APC Back-ups ES 750. I had configured ReadyNas send email notifications for issues regarding the UPS. I am getting several notifying of a switch to battery power and back to line power due to electrical noise.
It appears that in ReadyNas 6.5.2 there is no control or adjustments for issues such as sensitivity and voltage like available in APC's Powerchute. Looks like my only option is to not send notifications.
Any advice?
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: Adjusting the sensitivity of UPS on a RN312 with ReadyNas 6.5.2
@Hardhat wrote:
It appears that in ReadyNas 6.5.2 there is no control or adjustments for issues such as sensitivity and voltage like available in APC's Powerchute.
Correct. And you can't turn off UPS notifications either.
A mail filter on the receiving end might be a better option than turning all notifications off.