vandermerwe
Oct 09, 2016Master
6.6.0 UPS alerts not sent
Had a power supply failure prior to the daily boot up at 08:00. Looking at the logs it appears that a controlled shutdown took place about 2 minutes after the initial startup. The UPS powers other ...
- Jan 04, 2017
Btw ReadyNAS OS 6.6.1 is now available!
In the unlikely event you still have problems on 6.6.1 please start a new thread.
Michael_Oz
Nov 18, 2016Luminary
Logs sent
Michael_Oz
... RN316 logs sent, let me know if you want NV+ logs, it seemed to me the NV+ frontview reported UPS status more promptly than RN316.
Here is the recent NV+ frontview logs:
Sat Nov 19 14:11:43 EST 2016 UPS Communication error.
Sat Nov 19 14:11:22 EST 2016 Communication with UPS OK.
Sat Nov 19 12:39:07 EST 2016 UPS Communication error.
Sat Nov 19 10:25:18 EST 2016 Communication with UPS OK.
Sat Nov 19 10:25:15 EST 2016 Communication with UPS OK.
Sat Nov 19 10:23:59 EST 2016 System is up.
Sat Nov 19 10:22:59 EST 2016 Cannot communicate with UPS.
Sat Nov 19 10:22:51 EST 2016 UPS Communication error.
Sat Nov 19 10:18:00 EST 2016 UPS is shutting down system.
Sat Nov 19 10:18:00 EST 2016 UPS forcing shutdown.
Sat Nov 19 10:17:55 EST 2016 UPS battery is low; system will shutdown soon.
Sat Nov 19 10:16:25 EST 2016 UPS is on battery power.
Sat Nov 19 10:11:53 EST 2016 Communication with UPS OK.
Sat Nov 19 07:03:16 EST 2016 Backup finished. [Job 001]
Sat Nov 19 02:49:54 EST 2016 UPS Communication error.
Sat Nov 19 02:49:39 EST 2016 Communication with UPS OK.
Fri Nov 18 23:45:16 EST 2016 UPS Communication error.
Fri Nov 18 23:45:05 EST 2016 Communication with UPS OK.
Fri Nov 18 22:12:49 EST 2016 UPS Communication error.
Fri Nov 18 22:12:29 EST 2016 Communication with UPS OK.
Fri Nov 18 19:07:52 EST 2016 UPS Communication error.
Fri Nov 18 17:20:55 EST 2016 Communication with UPS OK.
Fri Nov 18 17:20:49 EST 2016 UPS Communication error.
Fri Nov 18 17:09:02 EST 2016 Communication with UPS OK.
Fri Nov 18 00:50:06 EST 2016 UPS Communication error.
Fri Nov 18 00:49:50 EST 2016 Communication with UPS OK.
Thu Nov 17 23:17:35 EST 2016 UPS Communication error.
Thu Nov 17 23:17:14 EST 2016 Communication with UPS OK.
Thu Nov 17 20:12:51 EST 2016 UPS Communication error.
Thu Nov 17 20:12:35 EST 2016 Communication with UPS OK.
Thu Nov 17 18:40:20 EST 2016 UPS Communication error.
Thu Nov 17 18:40:09 EST 2016 Communication with UPS OK.
- ewokNov 29, 2016NETGEAR Expert
Did you receive similar UPS communication error messages with previous versions of the firmware? What is the output of 'upsc UPS' from the RN316 during the error periods?
Sat Nov 19 10:25:18 EST 2016 Communication with UPS OK. - Michael_OzNov 29, 2016Luminary
ewok wrote:Did you receive similar UPS communication error messages with previous versions of the firmware?
Pre 6.6.0 UPS was working normally.
6.6.0 has UPS problems, as documented by me above ~2016-11-14 (System/Power/UPS -> UPS_RAWSTATUS_WAIT)
6.6.1 beta 1, changed but still has a problem, as documented above ~2016-11-18 (System/Power/UPS -> Waiting for status update.)
ReadyNAS does not detect UPS on battery & does not shutdown as it should.
extracts of syslog are in the above posts showing upsc output
Welcome to ReadyNASOS 6.6.1-T200 (Beta 1)
root@ME-NAS-316A:~# upsc UPS
Error: Server disconnectedI sent logs as per mdgm-ntgr request 2016-11-19
Note ShoGinn has this issue as posted above, as do bobaloca powellandy1 TOMA1 as posted here (re beta 1)
- slashdottedNov 30, 2016Aspirant
Hello,
I have (had?) the same issues (Stale data, UPS_RAWSTATUS_WAIT) with my RN204 (firmware 6.6.0) with a CyberPower CP1550EPFCLCD UPS (usb connection)
I've changed some parameters in /etc/nut/ups.conf; in particular, following the information found in http://networkupstools.org/docs/man/ups.conf.html and http://networkupstools.org/docs/man/usbhid-ups.html, I've added:
synchronous = yes pollonly = yes pollinterval = 10
And (at least for now) it seems to work fine
- ewokNov 30, 2016NETGEAR ExpertWe haven't been able to reproduce the issue here, would you be willing to adjust some UPS server settings manually and see if there is any improvement? Try reducing the polling frequency by adding "pollinterval = 10" to /etc/nut/ups.conf, then running "systemctl nut-driver restart". Changing UPS settings in the UI may overwrite these settings, so try not to do that.
Error: Server disconnected - slashdottedNov 30, 2016Aspirant
... uh?! can't edit my previous post...
So it seems that after a reboot /etc/nut/ups.conf gets overwritten/recreated :smileysad: In order to maintain those configuration changes we need to create an alternate configuration file and have the nut daemon use it.
Here's what I did:
Connecting to my NAS using ssh, I edited (using vi) /lib/systemd/system/nut-driver.service to look like this:
[Unit] Description=Network UPS Tools - power device driver controller After=local-fs.target network.target systemd-udev-settle.service Wants=systemd-udev-settle.service StopWhenUnneeded=yes [Service] Environment="NUT_CONFPATH=/etc/nuts" ExecStart=/sbin/upsdrvctl start ExecStop=/sbin/upsdrvctl stop Type=forking
(notice the line starting with Environment right after [Service]: this line changes the path containing configuration files to /etc/nuts)
Next, I created a copy of the /etc/nut directory in /etc/nuts (this way if the original ups.conf file is overwritten we won't care)
cp -r /etc/nut /etc/nuts
Next, I've modified the file /etc/nuts/ups.conf (that's the copy we made in /etc/nuts) and added these two lines (Note: in my previous post I made a mistake since pollinterval is not supported by the usbhid-ups driver):
In my case the resulting file looks like this now:
[UPS] driver = usbhid-ups port = auto #dashboard: ups_model = CP1500EPFCLCD #dashboard: ups_mfr = CPS #dashboard: ups_mfr_date = serial = XXXXXXXXXXXX vendorid = 0764 synchronous = yes pollonly = yes productid = 0501
The documentation for the pollonly flag says that "If this flag is set, the driver will ignore interrupts it receives from the UPS (not recommended, but needed if these reports are broken on your UPS). "
For the synchronous flag, the documentation says " The driver work by default in asynchronous mode (i.e synchronous=no). This means that all data are pushed by the driver on the communication socket to upsd (Unix socket on Unix, Named pipe on Windows) without waiting for these data to be actually consumed. With some HW, such as ePDUs, that can produce a lot of data, asynchronous mode may cause some congestion, resulting in the socket to be full, and the driver to appear as not connected."
You can test the configuration by restarting the daemon with:
systemctl daemon-reload systemctl restart nut-driver
... and check that the daemon is running with:
systemctl status nut-driver
I hope this helps and solves your issues too (... while we wait for an official fix)
- mdgm-ntgrNov 30, 2016NETGEAR Employee Retired
Well as we can't reproduce this we would need remote access to a system still having problems after the fix in 6.6.1 Beta.
- Michael_OzNov 30, 2016Luminary
mdgm wrote:Well as we can't reproduce this we would need remote access to a system still having problems after the fix in 6.6.1 Beta.
I'm game.
Well, to test, I did the ups.conf change to add
Not the whole make a second copy change, I don't reboot often
It has now been over two hours without an error message.
system.log shows below, and no errors.
Dec 01 14:36:31 ME-NAS-316A usbhid-ups[9184]: Startup successful
Dec 01 14:36:33 ME-NAS-316A upsd[6853]: Connected to UPS [UPS]: usbhid-ups-UPS
Dec 01 14:36:40 ME-NAS-316A msmtpq[9199]: mail for [ -C /etc/msmtprc michael...@...com.au --timeout=60 ] : send was successful
Dec 01 14:38:32 ME-NAS-316A upsd[6853]: User monuser@192.168.1.10 logged into UPS [UPS]The mail was the Comms OK msg.
I unplugged the UPS, it behaved as expected. Got the frontview status changes, emails and the network monitoring of the NV+ too.
So that should do until a fix gets released.
Stll happy for a remote session if someone from NG wants to look around.
- ewokDec 01, 2016NETGEAR Expert
Were both of these options needed or does it still fail when only of them are applied? We can add this fix to the firmware, but need to know if both are required since we can't reproduce it here.
- Michael_OzDec 01, 2016Luminary
I'll test today.
- slashdottedDec 02, 2016Aspirant
Hello,
here are some intial test results:
UPS: Cyberpower CP1500EPFCLCD
WORKING CONFIGURATION
synchronous = yes
pollonly = yes
Tested, stable for 24h
PROBABLY WORKING CONFIGURATION
pollonly = yes
In-progress (but seems stable)... will check again in a few hours
NON-WORKING CONFIGURATIONS
synchronous = yes
Hangs after a while, and I periodically got the following message in the log: libusb_get_interrupt: Connection timed out
no-additional parameters (default config)
Logs show libusb_get_interrupt: Connection timed out
After some time 'upsc UPS' returns Data stale - Michael_OzDec 02, 2016Luminary
I'm still testing (needs to do power fail tests), but looks like I will have the same results.
I also tested pollinterval=10, seemed to work, I'll test some other numbers.
Hello again,
for myUPS (Cyberpower CP1500EPFCLCD) the important parameter that needs to be added to ups.conf to fix this issue is pollonly = yes
In summary:
SUGGESTED WORKING CONFIGURATION
pollonly = yes
Tested, stable(ALSO) WORKING CONFIGURATION
synchronous = yes
pollonly = yes
Tested, stable
synchronous = yes
UPS: Cyberpower VALUE1200ELCD
Details from ups.log:
device.mfr: CPS
device.model: Value1200E
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 5
driver.parameter.port: auto
driver.parameter.productid: 0501
driver.parameter.synchronous: no
driver.parameter.vendorid: 0764
driver.version: 2.7.4
driver.version.data CyberPower HID 0.4
driver.version.internal: 0.41
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 32
ups.mfr: CPS
ups.model: Value1200E
ups.productid: 0501Test a. No errors for > 2 hours, b. correct behaviour when UPS unplugged.
Same, general results as slashdotted, different errors (no timeout error):
Individually:
synchronous=yes - fail
Dec 02 16:45:22 ME-NAS-316A usbhid-ups[25161]: Startup successful
Dec 02 16:45:24 ME-NAS-316A upsd[29633]: Connected to UPS [UPS]: usbhid-ups-UPS
Dec 02 17:25:42 ME-NAS-316A upsd[29633]: Data for UPS [UPS] is stale - check driver
Dec 02 17:25:42 ME-NAS-316A upsmon[29636]: Poll UPS [UPS@localhost] failed - Data stalepollonly=yes - pass
pollinterval=5 - pass
For me, I think pollinterval=5 would be better as pollonly=yes ignores interrupts, which are apparently working on my UPS.
However if pollonly is easier, hay it works.
- Michael_OzDec 03, 2016Luminary
BTW, if my reading is correct, the pollfreq=30 has the USB driver wait 30 seconds between polls, listening for interrupts, while pollinterval is the delay between upsd 'updating the status'. Thus pollinterval shorter than pollfreq/2 (ie on average) will only be benificial in upsd picking up interupts prior to the next poll.So, in the bigger picture, a few seconds doesn't matter when power fails, a higher pollinterval may be called for. It only really affects reporting of UPS status, and that is only meaningfull when it is discharging, or less so, when recharging. [question is what types of messages the UPS sends unsolicited, i.e. via interrups?]
So I can't see why a pollinterval<15 is of much use. Even a pollinterval=9, will check for changes ~3 times per poll.
pollonly=yes 'ignore interrupts it receives from the UPS', presumably does not affect pollfreq, but without interrups power notification is delayed, thus the question of whether pollfreq should perhaps be shortened? The above pollinterval considerations apply. So, for example, pollfreq=10 & pollinterval=5, or (15/5, 10/3?) should be considered, and tested.
- powellandy1Dec 04, 2016Virtuoso
mdgm-ntgr - L3 have remoted into my 3 NASes over the weekend (under case 27517658)
A
- ewokDec 05, 2016NETGEAR Expert
Please try the pollinterval setting as Michael_Oz suggested. If this works for you, pollinterval is probably the most flexible fix for this since some UPS models may work with a setting of 10, while another may require a setting of 15, etc. and adding this to the UI would be simple and easy for users to understand.
- slashdottedDec 06, 2016Aspirant
Ok, I've set pollinterval = 5 and the system seems fine (uptime 2h30m)... I will check again tomorrow morning (i.e. in ~12h) to see if everything is still ok.
After 14 hours still running fine (with pollinterval = 5)
:manhappy:
- powellandy1Dec 08, 2016Virtuoso
Heard back from L3 support. They have found and fixed a bug in libusb that will be in beta 3.
- mdgm-ntgrDec 08, 2016NETGEAR Employee Retired
Yes.
- mdgm-ntgrDec 09, 2016NETGEAR Employee Retired
Please try ReadyNASOS 6.6.1-T220 (Beta 3) which is now available.
- ScotsDonDec 09, 2016Guide
mdgm wrote:Please try ReadyNASOS 6.6.1-T220 (Beta 3) which is now available.
Quick question - can anybody (i.e. myself) install the Beta 3 version? Is it sufficiently stable? I have an APC Back-UPS,405 Watts /700 VA connected by USB.
- StephenBDec 09, 2016Guru - Experienced User
It's an open beta, so anyone can download/install it.
I've had no issues with beta-2 stability on both ARM and X86 NAS. I've installed beta-3, but it's too early to know how it compares. The changes over beta-2 look very targetted, so I am expecting no stability problems. But you never know, that's why there are betas.
- Michael_OzDec 09, 2016Luminary
StephenB wrote:It's an open beta, so anyone can download/install it.
So why does it say:
WARNINGS:
- Unless you are advised by NETGEAR Support in a support case to update to beta software, NETGEAR Support may deny support if you are running beta software. You can seek help here on the NETGEAR Community for issues encountered on the beta.