UPS Monitoring
Hi, I have a Readynas NV+ connected via USB to a Belkin UPS. It shows as connected in RAIDar. It shows as a Belkin and says 100% 2 minutes. The front panel of the NV+ shows it connected and in the pow...
StephenB
Sep 21, 2011Guru - Experienced User
Try removing the iMac and the Time Machine; restart the DUO and see if the menu item appears.
2 minutes is short enough that the connected devices might not have time to shut down gracefully. So I'd suggest a larger UPS (making sure it is compatible with the circuit amperage). You could still use the Belkin on the least power-hungry device.
2 minutes is short enough that the connected devices might not have time to shut down gracefully. So I'd suggest a larger UPS (making sure it is compatible with the circuit amperage). You could still use the Belkin on the least power-hungry device.