MikeNeuffer
Sep 01, 2023Tutor
M4300 and Timer Schedules / time-range Status always goes to Inactive - How to fix?
We have several M4300 (52G/96x) and switches and I am trying to setup working schedules to switch off POE for several ports during the night and the weekends when the offices are empty. The invo...
MikeNeuffer
Sep 04, 2023Tutor
schumaku First of all thank you for you answer, however
as I wrote previously, the whole timer schedule goes to inactive as soon as I enter the first entry, so this already invalidates your comment.
I've documented the behaviour with a few screenshots:
Add a new Timer Schedule
Add new Timer Schedule
The Timer Schedule is active
The new Timer Schedule is active - but with no Schedules attached yet
Add a periodic Schedule to the Timer Schedule
Add the new periodic schedule to the Timer Schedule by clicking on the <Add> button (not in the screenshot). It makes no difference if I use a day in the past, todays date or some day in the future for "Day Start".
According to the documentation this schedule will run (ie switch off POE) Mon-Fri from one minute past midnight until 7am.
However:
The Timer Schedule has become inactive
Now the Timer Schedule has become inactive.
What is wrong here ? How to switch on the schedule?
Coming back to your posting, why should 00:00-00:00 not be a meaningful entry?
How else should I qualify that POE should be down on the port for the whole day?
00:00 - 24:00 is not a valid entry and results in an error:
"Error! Invalid 'Time End' format: 24:00"
Switching on POE for one minute per day (23:59 - 00:00) by setting it to 00:00 - 23:59 seems kind of non-sensical.
The devices (mostly, but not exclusively IP telephones) would start to boot, just to be choked off again almost immediately - not exactly very healthy for the hardware.
MikeNeuffer
Sep 07, 2023Tutor
I order to document my findings:
We have undocumented behaviour here:
Once a schedule has been configured for a Timer Schedule, the status of the timer schedule (active/inactive) is determined by wether one of the schedules is _currently_ triggering/running or not. Before it is always active.
I found a severe bug in the current FW release 12.0.17.13 (not sure if it is also present in older releases):
If you update a Schedule of a Timer Schedule
it will immediately reset the affected ethernet ports
as soon as you click on <Apply>
if the schedule will trigger next in more then a handful minutes.
I didn't experiment in oder to find the exact required time differential,
but is was able to see the ports being reset when I was clicking on <Apply> about 10min before the Schedule would trigger, and it didn't reset them when the time differential was about 3 minutes.
Actually I first tested the 3 minutes differential, then with a modified schedule the 10min differential.
This is absolutely reproducible on the M4300 I did my tests on when I was discussing the active/inactive issue with 2nd/3rd level support.