APC Back-UPS RS 550GI
Reporting back the results of the following model : APC Back-UPS RS 550GI (region = UK)
Originally the setting within Frontview was set to "Auto" - Had to fix the percentage to get it to shutdown properly.
Whats the criteria for the ReadyNAS to shut itself down - Is it based on a percentage figure or set amount left on the UPS?
Reason for asking is because, when set to "Auto" it drained to 19% before I intervened & set the Frontview setting to shutdown at 10%.
The NVX then successfully shutdown when it hit 10%.
A switch was also attached but here's the result.
Tue Mar 9 17:47:33 WET 2010 UPS is shutting down system.
Tue Mar 9 17:47:31 WET 2010 UPS battery is low; system will shutdown soon.
Tue Mar 9 17:45:47 WET 2010 UPS is on battery power.
Tue Mar 9 17:25:08 WET 2010 UPS is on battery power.
Originally the setting within Frontview was set to "Auto" - Had to fix the percentage to get it to shutdown properly.
Whats the criteria for the ReadyNAS to shut itself down - Is it based on a percentage figure or set amount left on the UPS?
Reason for asking is because, when set to "Auto" it drained to 19% before I intervened & set the Frontview setting to shutdown at 10%.
The NVX then successfully shutdown when it hit 10%.
A switch was also attached but here's the result.
Tue Mar 9 17:47:33 WET 2010 UPS is shutting down system.
Tue Mar 9 17:47:31 WET 2010 UPS battery is low; system will shutdown soon.
Tue Mar 9 17:45:47 WET 2010 UPS is on battery power.
Tue Mar 9 17:25:08 WET 2010 UPS is on battery power.
Message 1 of 9
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
2010-03-10
06:06 AM
2010-03-10
06:06 AM
Re: APC Back-UPS RS 550GI
I tried this again, taking the sensible approach this time & attached the NVX to the mains & kept a non critical load on the UPS & let the NVX monitor the UPS.
Select shutdown on battery low threshold : "Auto"
Successfully shutdown when it got to 9%,
So I reckon this answers my query when alerts will come, it was waiting the "critical alert" signal from the UPS, but It get's pretty close to depletion for my liking, so I'll stick with manually setting the percentage as it's not critical if the NVX goes off-line early.
Final set of notifications from the Frontview log.
Wed Mar 10 08:50:48 WET 2010 System is up.
Wed Mar 10 08:48:50 WET 2010 UPS is shutting down system.
Wed Mar 10 08:48:48 WET 2010 UPS battery is low; system will shutdown soon
Select shutdown on battery low threshold : "Auto"
Successfully shutdown when it got to 9%,
So I reckon this answers my query when alerts will come, it was waiting the "critical alert" signal from the UPS, but It get's pretty close to depletion for my liking, so I'll stick with manually setting the percentage as it's not critical if the NVX goes off-line early.
Final set of notifications from the Frontview log.
Wed Mar 10 08:50:48 WET 2010 System is up.
Wed Mar 10 08:48:50 WET 2010 UPS is shutting down system.
Wed Mar 10 08:48:48 WET 2010 UPS battery is low; system will shutdown soon
Message 2 of 9
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
2010-03-21
03:46 PM
2010-03-21
03:46 PM
Re: APC Back-UPS RS 550GI
Chirpa, kindly posted a link on a similar thread which queried when the "Auto" setting should kick in, so the Readynas should shutdown when it receives the "CRITICAL" mode.
viewtopic.php?f=7&t=22479&start=0
viewtopic.php?f=7&t=22479&start=0
Message 3 of 9
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
2010-03-22
08:02 AM
2010-03-22
08:02 AM
Re: APC Back-UPS RS 550GI
Just want to share that the APC Back-UPS RS 550GI (UK) works well with my ReadyNAS 2100. Automatic shutdown completed as required when battery power threshold of 90% was reached.
Mar 22 14:54:23 nas2 RAIDiator: UPS is on battery power.\n[Mon Mar 22 14:54:23 GMT 2010]
Mar 22 14:54:55 nas2 RAIDiator: UPS battery is low; system will shutdown soon.\n[Mon Mar 22 14:54:55 GMT 2010]
Mar 22 14:54:57 nas2 RAIDiator: UPS is shutting down system.\n[Mon Mar 22 14:54:57 GMT 2010]
Mar 22 14:56:19 nas2 kernel: generic-usb 0003:051D:0002.0001: hiddev96: USB HID v1.00 Device [American Power Conversion Back-UPS RS 550GI FW:857.L1 .I USB FW:L1 ] on usb-0000:00:1d.7-2.2/input0
Another one for the HCL?
Mar 22 14:54:23 nas2 RAIDiator: UPS is on battery power.\n[Mon Mar 22 14:54:23 GMT 2010]
Mar 22 14:54:55 nas2 RAIDiator: UPS battery is low; system will shutdown soon.\n[Mon Mar 22 14:54:55 GMT 2010]
Mar 22 14:54:57 nas2 RAIDiator: UPS is shutting down system.\n[Mon Mar 22 14:54:57 GMT 2010]
Mar 22 14:56:19 nas2 kernel: generic-usb 0003:051D:0002.0001: hiddev96: USB HID v1.00 Device [American Power Conversion Back-UPS RS 550GI FW:857.L1 .I USB FW:L1 ] on usb-0000:00:1d.7-2.2/input0
Another one for the HCL?
Message 4 of 9
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
2010-07-30
10:36 AM
2010-07-30
10:36 AM
Re: APC Back-UPS RS 550GI
reporting back since my original post- over the last month or so, I've had a couple of power interuptions from the mains supply & the UPS has handled each event perfectly. 😄
Under each occasion it kept power supplied to my unit & when one outage was extended, it shut down at the requested %
Under each occasion it kept power supplied to my unit & when one outage was extended, it shut down at the requested %
Message 5 of 9
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
2010-12-12
10:53 PM
2010-12-12
10:53 PM
Re: APC Back-UPS RS 550GI
Another report:
Readynas pro works fine with this UPS, didn't let it to power drain the UPS completely so I don't know if it shuts down automatically but it reports the same amount of time left as the LCD on the UPS itself so I guess it would work fine in such a scenario as well.
Readynas pro works fine with this UPS, didn't let it to power drain the UPS completely so I don't know if it shuts down automatically but it reports the same amount of time left as the LCD on the UPS itself so I guess it would work fine in such a scenario as well.
Message 6 of 9
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
2011-10-13
09:05 AM
2011-10-13
09:05 AM
Re: APC Back-UPS RS 550GI
Frontview health panel shows: "UPS 1 Error, Battery charge: 0%, 0 minutes Out of Spec"
If I try to change the threshold it gives me UPS communication error.
The UPS is fully charged and connected to NAS. Doesn't help if I change to another USB port.
Any ideas?
If I try to change the threshold it gives me UPS communication error.
The UPS is fully charged and connected to NAS. Doesn't help if I change to another USB port.
Any ideas?
Message 7 of 9
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
2011-10-17
01:26 AM
2011-10-17
01:26 AM
Re: APC Back-UPS RS 550GI
are you talking about THIS model ?
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BR550GI or the RS 550GI is another one
thanks
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BR550GI or the RS 550GI is another one
thanks
Message 8 of 9
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
2011-11-21
11:08 AM
2011-11-21
11:08 AM
Re: APC Back-UPS RS 550GI
Yeah, I have BR 550GI, but ReadyNAS recognizes it as RS 550GI
cat /proc/bus/usb/devices
T: Bus=05 Lev=01 Prnt=01 Port=01 Cnt=01 Dev#= 2 Spd=12 MxCh= 0
😧 Ver= 2.00 Cls=00(>ifc ) Sub=00 Prot=00 MxPS=64 #Cfgs= 1
P: Vendor=051d ProdID=0002 Rev= 0.90
S: Manufacturer=American Power Conversion
S: Product=Back-UPS RS 550GI FW:857.L3 .I USB FW:L3
S: SerialNumber=3B1118X41043
C:* #Ifs= 1 Cfg#= 1 Atr=e0 MxPwr= 2mA
I:* If#= 0 Alt= 0 #EPs= 1 Cls=03(HID ) Sub=00 Prot=00 Driver=usbhid
E: Ad=81(I) Atr=03(Int.) MxPS= 8 Ivl=100ms
Thanks
cat /proc/bus/usb/devices
T: Bus=05 Lev=01 Prnt=01 Port=01 Cnt=01 Dev#= 2 Spd=12 MxCh= 0
😧 Ver= 2.00 Cls=00(>ifc ) Sub=00 Prot=00 MxPS=64 #Cfgs= 1
P: Vendor=051d ProdID=0002 Rev= 0.90
S: Manufacturer=American Power Conversion
S: Product=Back-UPS RS 550GI FW:857.L3 .I USB FW:L3
S: SerialNumber=3B1118X41043
C:* #Ifs= 1 Cfg#= 1 Atr=e0 MxPwr= 2mA
I:* If#= 0 Alt= 0 #EPs= 1 Cls=03(HID ) Sub=00 Prot=00 Driver=usbhid
E: Ad=81(I) Atr=03(Int.) MxPS= 8 Ivl=100ms
Thanks