Re: 6.6.0 UPS alerts not sent, Hard Shutdown
@ScotsDon wrote:
the problem being that it crashes out with a hard shutdown, so endangering any data and being no better than what happens when the NAS is powered off the mains and a power cut occurs.
Maybe download the logs and check what it does.
In my two recent tests, such shutdowns did not require it to resync or anything when it came back up. I assumed (hmmm) it did a clean panic shutdown, ie flushing caches etc. [he says going to look at his logs...]
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent, Hard Shutdown
OK checked my logs.
When my NAS is not communicating with the UPS (my above posts) it doesn't shutdown.
When it is, briefly after I change a setting, it does, but does it properly, i.e.
Sat Nov 19 2016 10:24:54 System: ReadyNASOS service or process was restarted.
Sat Nov 19 2016 10:18:01 System: UPS UPS () battery is low. System will shut down soon.
Sat Nov 19 2016 10:16:29 System: UPS UPS () is on battery power.
So I suspect your problem may be different. But as someone said above, they do seem to have stuffed this area fairly well...
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent, Hard Shutdown
Maybe download the logs and check what it does.
In my two recent tests, such shutdowns did not require it to resync or anything when it came back up. I assumed (hmmm) it did a clean panic shutdown, ie flushing caches etc. [he says going to look at his logs...]
The logs shown under the System / Logs tab don't show anything. Are there any other Logs?
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent, Hard Shutdown
System/Logs Download_logs button on the left. Unzip check sysem.log (and generally look around at others). ups.log for me was almost empty.
[note I'm just another user here]
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent, Hard Shutdown
...that's system.log
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent, Hard Shutdown
@ScotsDon wrote:
This shows it is not the NAS losing its power from the UPS, but something to do with either the UPS or NAS firmware.
Sounds like that to me too. Hopefully someone from Netgear (maybe @Skywalker or @kohdee) will chime in.
There is a UPS fix in 6.6.1 beta, but it doesn't sound like what you are seeing.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent, Hard Shutdown
@Michael_Oz wrote:
@StephenB wrote:
There is a UPS fix in 6.6.1 beta, but it doesn't sound like what you are seeing.
Stephen, is that a new fix, or the one mentioned above which didn't fix my above problem?
It's the one above in (6.6.1 beta 1). The thread is a bit confusing, since we don't know if the two UPS problems have the same root cause (or not)..
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent, Hard Shutdown
@Michael_Oz wrote:System/Logs Download_logs button on the left. Unzip check sysem.log (and generally look around at others). ups.log for me was almost empty.
[note I'm just another user here]
Ah yes, lots and lots of logs!! Having a quick look, it seems the NAS could, just possibly, be doing a very fast but 'graceful' shutdown, or not, as the case may be. Only NetGear will know. If they want me to send them any logs, I have them ready.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
Did you receive similar UPS communication error messages with previous versions of the firmware? What is the output of 'upsc UPS' from the RN316 during the error periods?
Sat Nov 19 12:39:07 EST 2016 UPS Communication error.
Sat Nov 19 10:25:18 EST 2016 Communication with UPS OK.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent, Hard Shutdown
Please send the logs to my attention using the info in the link in my sig and I'll take a look.
@ScotsDon wrote:
Ah yes, lots and lots of logs!! Having a quick look, it seems the NAS could, just possibly, be doing a very fast but 'graceful' shutdown, or not, as the case may be. Only NetGear will know. If they want me to send them any logs, I have them ready.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
@ewok wrote:Did you receive similar UPS communication error messages with previous versions of the firmware?
Pre 6.6.0 UPS was working normally.
6.6.0 has UPS problems, as documented by me above ~2016-11-14 (System/Power/UPS -> UPS_RAWSTATUS_WAIT)
6.6.1 beta 1, changed but still has a problem, as documented above ~2016-11-18 (System/Power/UPS -> Waiting for status update.)
ReadyNAS does not detect UPS on battery & does not shutdown as it should.
extracts of syslog are in the above posts showing upsc output
@> ewok wrote:
> What is the output of 'upsc UPS'
Welcome to ReadyNASOS 6.6.1-T200 (Beta 1)
root@ME-NAS-316A:~# upsc UPS
Error: Server disconnected
I sent logs as per @mdgm-ntgr request 2016-11-19
Note @ShoGinn has this issue as posted above, as do @bobaloca @powellandy1 @TOMA1 as posted here (re beta 1)
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
Hello,
I have (had?) the same issues (Stale data, UPS_RAWSTATUS_WAIT) with my RN204 (firmware 6.6.0) with a CyberPower CP1550EPFCLCD UPS (usb connection)
I've changed some parameters in /etc/nut/ups.conf; in particular, following the information found in http://networkupstools.org/docs/man/ups.conf.html and http://networkupstools.org/docs/man/usbhid-ups.html, I've added:
synchronous = yes pollonly = yes pollinterval = 10
And (at least for now) it seems to work fine
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
@Michael_Oz wrote:
Pre 6.6.0 UPS was working normally.
6.6.0 has UPS problems, as documented by me above ~2016-11-14 (System/Power/UPS -> UPS_RAWSTATUS_WAIT)
6.6.1 beta 1, changed but still has a problem, as documented above ~2016-11-18 (System/Power/UPS -> Waiting for status update.)
ReadyNAS does not detect UPS on battery & does not shutdown as it should.
extracts of syslog are in the above posts showing upsc output
@> ewok wrote:
> What is the output of 'upsc UPS'
Welcome to ReadyNASOS 6.6.1-T200 (Beta 1)
root@ME-NAS-316A:~# upsc UPS
Error: Server disconnected
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
... uh?! can't edit my previous post...
So it seems that after a reboot /etc/nut/ups.conf gets overwritten/recreated In order to maintain those configuration changes we need to create an alternate configuration file and have the nut daemon use it.
Here's what I did:
Connecting to my NAS using ssh, I edited (using vi) /lib/systemd/system/nut-driver.service to look like this:
[Unit] Description=Network UPS Tools - power device driver controller After=local-fs.target network.target systemd-udev-settle.service Wants=systemd-udev-settle.service StopWhenUnneeded=yes [Service] Environment="NUT_CONFPATH=/etc/nuts" ExecStart=/sbin/upsdrvctl start ExecStop=/sbin/upsdrvctl stop Type=forking
(notice the line starting with Environment right after [Service]: this line changes the path containing configuration files to /etc/nuts)
Next, I created a copy of the /etc/nut directory in /etc/nuts (this way if the original ups.conf file is overwritten we won't care)
cp -r /etc/nut /etc/nuts
Next, I've modified the file /etc/nuts/ups.conf (that's the copy we made in /etc/nuts) and added these two lines (Note: in my previous post I made a mistake since pollinterval is not supported by the usbhid-ups driver):
synchronous = yes pollonly = yes
In my case the resulting file looks like this now:
[UPS] driver = usbhid-ups port = auto #dashboard: ups_model = CP1500EPFCLCD #dashboard: ups_mfr = CPS #dashboard: ups_mfr_date = serial = XXXXXXXXXXXX vendorid = 0764 synchronous = yes pollonly = yes productid = 0501
The documentation for the pollonly flag says that "If this flag is set, the driver will ignore interrupts it receives from the UPS (not recommended, but needed if these reports are broken on your UPS). "
For the synchronous flag, the documentation says " The driver work by default in asynchronous mode (i.e synchronous=no). This means that all data are pushed by the driver on the communication socket to upsd (Unix socket on Unix, Named pipe on Windows) without waiting for these data to be actually consumed. With some HW, such as ePDUs, that can produce a lot of data, asynchronous mode may cause some congestion, resulting in the socket to be full, and the driver to appear as not connected."
You can test the configuration by restarting the daemon with:
systemctl daemon-reload systemctl restart nut-driver
... and check that the daemon is running with:
systemctl status nut-driver
I hope this helps and solves your issues too (... while we wait for an official fix)
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
Well as we can't reproduce this we would need remote access to a system still having problems after the fix in 6.6.1 Beta.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
Well, to test, I did the ups.conf change to add
synchronous = yes pollonly = yes
Not the whole make a second copy change, I don't reboot often
It has now been over two hours without an error message.
system.log shows below, and no errors.
Dec 01 14:36:31 ME-NAS-316A usbhid-ups[9184]: Startup successful
Dec 01 14:36:33 ME-NAS-316A upsd[6853]: Connected to UPS [UPS]: usbhid-ups-UPS
Dec 01 14:36:40 ME-NAS-316A msmtpq[9199]: mail for [ -C /etc/msmtprc michael...@...com.au --timeout=60 ] : send was successful
Dec 01 14:38:32 ME-NAS-316A upsd[6853]: User monuser@192.168.1.10 logged into UPS [UPS]
The mail was the Comms OK msg.
I unplugged the UPS, it behaved as expected. Got the frontview status changes, emails and the network monitoring of the NV+ too.
So that should do until a fix gets released.
Stll happy for a remote session if someone from NG wants to look around.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
Were both of these options needed or does it still fail when only of them are applied? We can add this fix to the firmware, but need to know if both are required since we can't reproduce it here.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
Hello,
here are some intial test results:
UPS: Cyberpower CP1500EPFCLCD
WORKING CONFIGURATION
synchronous = yes
pollonly = yes
Tested, stable for 24h
PROBABLY WORKING CONFIGURATION
pollonly = yes
In-progress (but seems stable)... will check again in a few hours
NON-WORKING CONFIGURATIONS
synchronous = yes
Hangs after a while, and I periodically got the following message in the log: libusb_get_interrupt: Connection timed out
no-additional parameters (default config)
Logs show libusb_get_interrupt: Connection timed out
After some time 'upsc UPS' returns Data stale
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
I'm still testing (needs to do power fail tests), but looks like I will have the same results.
I also tested pollinterval=10, seemed to work, I'll test some other numbers.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
Hello again,
for myUPS (Cyberpower CP1500EPFCLCD) the important parameter that needs to be added to ups.conf to fix this issue is pollonly = yes
In summary:
SUGGESTED WORKING CONFIGURATION
pollonly = yes
Tested, stable
(ALSO) WORKING CONFIGURATION
synchronous = yes
pollonly = yes
Tested, stable
NON-WORKING CONFIGURATIONS
synchronous = yes
Hangs after a while, and I periodically got the following message in the log: libusb_get_interrupt: Connection timed out
no-additional parameters (default config)
Logs show libusb_get_interrupt: Connection timed out
After some time 'upsc UPS' returns Data stale
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
UPS: Cyberpower VALUE1200ELCD
Details from ups.log:
device.mfr: CPS
device.model: Value1200E
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 5
driver.parameter.port: auto
driver.parameter.productid: 0501
driver.parameter.synchronous: no
driver.parameter.vendorid: 0764
driver.version: 2.7.4
driver.version.data CyberPower HID 0.4
driver.version.internal: 0.41
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 32
ups.mfr: CPS
ups.model: Value1200E
ups.productid: 0501
Test a. No errors for > 2 hours, b. correct behaviour when UPS unplugged.
Same, general results as @slashdotted, different errors (no timeout error):
Individually:
synchronous=yes - fail
Dec 02 16:45:22 ME-NAS-316A usbhid-ups[25161]: Startup successful
Dec 02 16:45:24 ME-NAS-316A upsd[29633]: Connected to UPS [UPS]: usbhid-ups-UPS
Dec 02 17:25:42 ME-NAS-316A upsd[29633]: Data for UPS [UPS] is stale - check driver
Dec 02 17:25:42 ME-NAS-316A upsmon[29636]: Poll UPS [UPS@localhost] failed - Data stale
pollonly=yes - pass
pollinterval=5 - pass
For me, I think pollinterval=5 would be better as pollonly=yes ignores interrupts, which are apparently working on my UPS.
However if pollonly is easier, hay it works.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Re: 6.6.0 UPS alerts not sent
BTW, if my reading is correct, the pollfreq=30 has the USB driver wait 30 seconds between polls, listening for interrupts, while pollinterval is the delay between upsd 'updating the status'. Thus pollinterval shorter than pollfreq/2 (ie on average) will only be benificial in upsd picking up interupts prior to the next poll.So, in the bigger picture, a few seconds doesn't matter when power fails, a higher pollinterval may be called for. It only really affects reporting of UPS status, and that is only meaningfull when it is discharging, or less so, when recharging. [question is what types of messages the UPS sends unsolicited, i.e. via interrups?]
So I can't see why a pollinterval<15 is of much use. Even a pollinterval=9, will check for changes ~3 times per poll.
pollonly=yes 'ignore interrupts it receives from the UPS', presumably does not affect pollfreq, but without interrups power notification is delayed, thus the question of whether pollfreq should perhaps be shortened? The above pollinterval considerations apply. So, for example, pollfreq=10 & pollinterval=5, or (15/5, 10/3?) should be considered, and tested.